Legacy Forums => Experienced User Forum => Topic started by: RavenIV on February 02, 2004, 08:11:11 AM

Title: apcupsd not working
Post by: RavenIV on February 02, 2004, 08:11:11 AM
SME 5.6u5
ups-type: APC SMART-UPS 1000 RM

first i enabled the nut-service, but i got no response from the ups.
then i installed the apcupsd-contrib from D.May.
i configured it and it does not work.
in /var/log/messages there is a line "Starting UPS monitoring:/sbin/apcupsd: Error :: Changing UPSTYPE from SmartUPS to BackUPS due wrong Cable of Smart Signals."
if i type "/etc/init.d/apcupsd start", it tells me "Unable to create serial port lock file"

the cable is the original that was shipped with the UPS.

what else do i have to check or configure?

cheers klaus
Title: Re: apcupsd not working
Post by: mocco on February 02, 2004, 09:54:48 AM
Quote from: "RavenIV"
SME 5.6u5
ups-type: APC SMART-UPS 1000 RM

the cable is the original that was shipped with the UPS.
what else do i have to check or configure?

Not sure but this might help:
http://www.sibbald.com/apcupsd/3.10.x-manual/quickstart.html
http://www.sibbald.com/apcupsd/3.10.x-manual/supported.html#ftn.custom_cable
http://www.sibbald.com/apcupsd/3.10.x-manual/cables.html
Title: apcupsd not working
Post by: byte on February 02, 2004, 10:33:40 AM
Hi,

Im using the exact same ups on SME 5.6 and have no problems.

Have you disabled nut you dont need that, next have you choose the correct cable? on the bottom of the serial cable there should be a number 940 or something like that is that right?

HTH

Byte
Title: apcupsd not working
Post by: sudemo on February 02, 2004, 11:03:30 PM
You need for sure the signal cable 940-0024C. You can find this number on the male connector.
If you have a other one it will not work !

Martin
Title: apcupsd not working
Post by: RavenIV on February 03, 2004, 01:55:05 AM
thanks to all for the hints.
i will check the cable and do the config and test like in the posted url's.

will report the result.

cheers klaus